Scheduled Power Infrastructure
Maintenance
XMission has scheduled maintenance work for
Friday, March 12th starting at 8 p.m. MST to
troubleshoot and repair the ATS (Automatic
Transfer Switch) which briefly malfunctioned
and caused a short, partial outage in our
data center the night of January 22nd.
Although we immediately contacted our vendor
after the outage, we needed to wait for the
repair parts to arrive. On Friday night our
electricians will consolidate all power over
to our redundant bus to completely
de-energize the ATS so the generator
specialists can safely and thoroughly test
all key components then replace or repair
whatever they find amiss. To clarify, we
will temporarily move all power to a single
source, secured through our operational ATS
and UPS system. Once the ATS in question has
been repaired the vendor will test it to
confirm everything is working properly
before we move load back to the power bus
and wrap up maintenance. XMission will have
the appropriate staff standing by in the
event of power-loss, however no downtime is
expected.